If you are increasing the insulation levels in your current home, choosing the right
insulation material can be challenging. Fibrous loose-fill insulations such as cellulose,
fiberglass, and rock wool are options you may wish to consider.
Character and Types of Loose-Fill Insulation
The most obvious difference between loose fills and other types of insulation is their
form. They are either produced as—or broken down into—shreds, granules, or
nodules. These small particles form fluffy materials that conform to the spaces in which
they are installed. Loose fills are most commonly sold in bags and are blown into building
cavities using special equipment. All three primary types of loose-fill insulation are
considered "environmentally positive" because recycled waste materials are used
in their production.
Cellulose loose-fill insulation is made from wastepaper, such as used newsprint and
boxes, which is shredded and pulverized into small, fibrous particles. Chemicals are added
to provide resistance to fire and insects. Also, less energy is required to produce
loose-fill cellulose than to produce other insulations.
Fiberglass loose-fill insulation is spun from molten glass into fibers. The glass is
typically melted in high-temperature gas furnaces. Most major manufacturers use 20% to 30%
recycled glass content.
Rock wool (or slag wool) loose-fill insulation is similar to fiberglass except that it
is spun from blast furnace slag (the scum that forms on the surface of molten metal) and
other rock-like materials instead of molten glass. The production of rock wool uses
by-products that would otherwise be wasted.

Primary Applications of Loose-Fill Insulations
Loose-fill insulations are well suited for places where it is difficult to install other
types of insulation, such as irregularly shaped areas, around obstructions (such as
plumbing stacks), and in hard-to-reach places. They can be installed in either enclosed
cavities such as walls or unenclosed spaces such as attics. Blown-in loose fills are
particularly useful for retrofit situations because, except for the holes that are
sometimes drilled for installations, they are one of the few materials that can be
installed without greatly disturbing existing finishes. Rock wool or slag wool loose-fill
insulation is often used for insulating existing walls and ceilings in mobile homes.
| Recommended Specifications by Insulation Type |
|
Cellulose |
Fiberglass |
Rock Wool |
| R-value/inch |
3.2–3.8 |
2.2–2.7 |
3.0–3.3 |
| Inches (cm) needed for R-38 |
10–12 (25–30) |
14–17 (35–43) |
11.5–13 (29–33) |
| Density in lb/ft3 (kg/m3) |
1.5–2.0 (24–36) |
0.5–1.0 (10–14) |
1.7 (27) |
| Weight at R-38 in lb/ft2 (kg/m2) |
1.25–2.0 (6–10) |
0.5–1.2 (3–6) |
1.6–1.8 (8–9) |
| OK for 1/2" drywall, 24" on center? |
No |
Yes |
No |
| OK for 1/2" drywall, 16" on center? |
Yes |
Yes |
Yes |
| OK for 5/8" drywall, 24" on center? |
Yes |
Yes |
Yes |
Comparative Performance of Loose-Fill Insulations
Insulation materials are compared on the basis of their R-values per unit of thickness,
density per unit of volume, and weight per unit of area.
There are several performance characteristics to consider when selecting an insulation
material. Among the most important to compare are insulating capacity, weight, convective
heat loss, settling and loss of insulating capacity, fire resistance, and moisture
resistance.
Insulating Capacity
A material's resistance to heat flow is expressed as its R-value. The higher the R-value,
the better the material insulates, and the lesser the thickness you will need. (However,
in an open, unrestricted attic application, the height limit of insulation thickness is of
no great concern. But if you use your attic for storage, heavy objects will compress
insulation and decrease its benefits.) Different insulations also have different
densities, or weights. There are weight limits for certain ceiling types (see the chart
and the section on Weight that follows).
Weight limits and other factors at R-38 insulation levels are shown in the chart on
this page for the three primary types of loose fills. (R-38 is a commonly recommended
ceiling insulation level in many parts of the United States.
Weight
Ceiling drywall can sag under heavy loads, such as those sometimes created by insulation.
One drywall manufacturer recommends loads of no more than 1.3 pounds per square foot (6
kilograms per square meter) for 1/2-inch (1.3-centimeter) ceiling drywall with framing
spaced 24 inches (61 centimeters) on center. The limit increases to 2.2 pounds per square
foot (11 kilograms per square meter) for framing spaced 16 inches (41 centimeters) on
center and for 5/8-inch (1.6-centimeter) drywall.
Loose-fill cellulose and rock wool, being heavier materials, could cause the ceiling to
sag if installed at R-38 on 1/2-inch (1.3-centimeter) ceiling drywall with framing spaced
24 inches (61 centimeters) on center (see chart).
Some cellulose and rock wool insulation manufacturers include weight limit information
on the bag. Because fiberglass is much less dense, its weight on ceiling dry wall is not a
concern.
Convective Heat Loss
Convection is heat flow caused by air currents. Convective heat loss in insulation is
rare, but it can occur when large temperature differences above and below insulation
create tiny air currents (called "convection loops") within the insulation.
Studies have shown that convective heat loss can occur with lighter density loose-fill
fiberglass at the very low attic temperatures possible in extremely cold climates.
Depending on the attic temperature, the insulation's measured R-value could decrease by as
much as 50%.
To minimize these convection loops and their associated effects, some researchers
suggest installing blown-in cellulose or a fiberglass blanket on top of the loose-fill
fiberglass. Another solution is to purchase one of the currently available
"convection blanket" products that can inhibit this convective heat loss.
Cellulose and rock wool are more resistant to airflow than fiberglass because they are
denser. They may also be more effective at reducing air leakage and associated heat loss,
because their higher densities cause them to settle and seal more around rafters and in
corners.
Sprayed-in-place foam insulations are an alternative to loose fills in some
applications. They offer higher R-values at lower thickness than loose fills and, when
properly installed, can help stop air leakage.
But no insulation, by itself, provides an effective air retarder because it cannot
completely block airflow. Installing an air retarder along with your insulation and using
caulking and weatherstripping seals all gaps and greatly reduces air infiltration into
your home (see the section on Air Retarders that follows).
Settling and Loss of Insulating Capacity
Many loose-fill insulations installed in attic cavities will lose some installed
R-value over time because of settling. Cellulose loose fill settles more than rock wool or
fiberglass loose fill-about 20% compared to roughly 2% to 4%. Therefore, install about 20%
more blown-in cellulose insulation to offset this settling. Cellulose manufacturers are
required by federal law to state "settled thickness" on their bags. Because this
can be confusing to consumers, many cellulose producers also specify "installed
thickness" on their bags. Regardless, installed thickness can be estimated by adding
20% to the stated settled thickness, but be sure not to exceed previously mentioned weight
limits.
Researchers say that it is possible to install loose-fill insulations in wall cavities
without settling. If the cavity is completely filled with insulation at the proper
density, no significant settling should occur. A general density guideline for walls is
roughly 3.5 pounds per cubic foot (17 kilograms per cubic meter) of wall cavity for
cellulose and 1.5 pounds per cubic foot (7 kilograms per cubic meter) for fiberglass or
rock wool. These specifications are roughly twice the density of horizontal applications.
One expert suggests this easy-to-follow guideline to ensure that wall cavities are
being filled at a density sufficient to prevent settling. Use roughly one 30-pound
(13-kilogram) bag of cellulose or about 15 pounds (8 kilograms) of fiberglass or rock wool
for every three-wall cavity you fill. (Assumptions: 8-foot [2.4-meter] walls, with
16-inch [41-centimeter] on center wall cavities, and 2x4-inch framing studs.)
Fire Resistance
Loose-fill insulations offer very good resistance to fire. Although fiberglass and rock
wool are naturally fire resistant, cellulose's fire resistance is achieved by adding
chemicals. To ensure that it does not present a fire hazard, cellulose must pass tests
established by the Consumer Product Safety Commission.
Moisture Resistance
The average household generates a considerable amount of water vapor each day through
activities such as cooking, laundry, and bathing. This vapor migrates into insulated
cavities and, if it reaches the dew point (the air temperature at which water vapor cools
enough to condense), it converts to liquid within the insulation. This reduces the
insulation's effective R-value.
All loose-fill insulations are permeable to water vapor. Permeability is the extent to
which water vapor can pass through a given material. Fiberglass and rock wool absorb about
1% of their weight, and cellulose absorbs 5% to 20% of its weight. However, any insulation
can absorb large amounts of water if exposed to extremely high humidity.
Higher levels of outdoor moisture can also penetrate into insulated cavities. If your
roof leaks, for example, moisture can accumulate in the attic cavity and wet the
insulation to the point that it mats and compacts. Enough moisture penetration could even
cause the ceiling to sag.
If insulation is saturated only one time, it will eventually dry and regain most of its
original R-value. However, loose-fill insulations that are repeatedly saturated will lose
much of their R-value. Moisture also causes additional problems, such as mold and mildew
growth.
See the Vapor Retarders section that follows for steps you can take to ensure
that moisture does not create a problem in your insulation.
Before You Install Insulation
Upgrading or Repairing Other Building Components
There are other home weatherizing and sealing measures to complete before you undertake
any insulation project. A tight, well-sealed home is more energy efficient and needs less
insulation to keep you and your family comfortable. Tests have shown that far more cold
air infiltration and heat loss result from improperly sealed windows, doors, ducts, light
switches, and outlets than from insufficient insulation coverage or performance.
Vapor Retarders
If you are adding insulation to an existing ceiling structure and a vapor retarder is not
already installed, consider adding one. Generally, the vapor retarder should be placed on
the warm-in-winter side of the insulation—usually the side facing the interior living
space. However, in hot, humid climates (primarily the southeastern states), there is
controversy over where a vapor retarder should be placed. No matter where you live,
consult an insulation manufacturer and your building code official for recommendations on
where to place a vapor retarder.
When installing loose-fill insulations, a material such as 6-mil (0.006-inch, or
0.015-centimeter) polyethylene plastic sheeting can be used as a vapor retarder. Paints
that act as vapor retarders are also available. These paints may be more practical for
retrofitting homes where no vapor retarder exists because they can be installed without
removing finished surfaces.
Federal Housing Administration Minimum Property Standards require that any product,
including paint, must have a permeability (perm) rating of 1.0 or lower to qualify as a
vapor retarder. The lower the perm rating, the greater the material's resistance to vapor
penetration. For example, 15-pound (6.8-kilogram) asphalt felt paper has a perm rating of
1.0, while 6-mil polyethylene sheeting is rated at 0.06, and common household aluminum
foil is rated at 0.0001.
If the drywall on your ceiling or wall is removed and the insulated area is completely
exposed, you can install 6-mil polyethylene sheeting. Be sure that it runs continuously
along the surface area of the ceiling and walls, and that no tears occur during
installation. Additionally, all penetrations, such as electrical outlets and light
switches, should be carefully sealed. There are preformed foam gaskets for use behind
outlets and switchplates.
Air Retarders
An air retarder reduces energy loss because it prevents heated or air-conditioned indoor
air from escaping through the building shell. It also blocks drafts of hot or cold outside
air—caused by winds and pressure differences between the inside and outside of the
house—that reduce your home's comfort and heating or cooling efficiency.
An air retarder is different from a vapor retarder in that it blocks only air, not
moisture. The American Society for Testing and Materials specifies that a material must
have a perm rating of 5.0 or higher to qualify as an air retarder. Remember, the higher
the perm rating of a material, the more moisture can pass through it. An air retarder
should have a high perm rating because this allows the escape of moisture that may have
migrated into insulated cavities.
Installation
Loose-fill insulations are typically installed with special equipment that blows the
insulation through a hose and into the cavity. Although loose fills can be installed in
both new and retrofit situations, they are especially popular for retrofit projects
because they can be installed with minimal disturbances to existing finishes.
Installation often calls for the "two-hole method," which entails drilling
two holes spaced vertically between the exterior walls' framing studs. The holes should be
2 inches (5 centimeters) in diameter. Working between each stud, drill one hole 16 inches
(41 centimeters) from the top of the wall. Drill the other hole 24 inches (61 centimeters)
from the bottom of the wall. The insulation is blown into the holes, and then the installation
holes are sealed. Professionals who are experienced at operating the equipment to ensure proper density and complete coverage most commonly do installation. In conventional
and cathedral ceilings, insulation is easier to blow in if an access opening through the
ceiling already exists. Otherwise, it may be necessary to drill holes in the ceiling or
between the roof rafters.
Cost
The average loose-fill insulation cost per R-value per square foot was about 0.8 cents for
cellulose and rock wool and 1.1 cents for fiberglass. These prices were for materials
only. The average installed price per R-value per square foot was about 1.2 cents for
blown-in cellulose and rock wool and 1.3 cents for fiberglass. Because prices vary in
different regions, obtain bids from several insulation contractors or suppliers to
determine the specific cost in your area.
Installation Quality Control
Voids and Gaps
To ensure a quality installation, there are several things to watch out for when
installing loose-fill insulation—whether you do the job yourself or hire a
professional.
You may create undesirable voids or gaps if you install the insulation at too low a
density or if you do not completely fill the cavity. Voids are most likely to occur at the
top of wall cavities, above windows, around doorways, and in the corners of ceiling
cavities. Voids also occur if the installation holes are improperly located between the
vertical framing studs or if there are too few fill holes. Keep in mind, though, that
installers' practices may vary regarding the number, location, and size of installation
holes.
It may be difficult to achieve recommended R-values with loose-fill insulation in the
eave area of the attic. There are insulation techniques that can be used to insulate this
area adequately.
Fluffing
"Fluffing" occurs when insulation is installed to minimum thickness but not to
minimum weight requirements. The result is a less dense application of insulation that
requires fewer bags. When insulation is "fluffed," air passes more easily
through it. This means increased heat loss. Additionally, the fluffed loose-fill
insulation will eventually settle and result in a thinner layer with a lower overall
R-value. Fiberglass is more "fluffable" than cellulose or rock wool.
Intentional fluffing by unscrupulous contractors has been a problem in some parts of
the country. To avoid these problems, compare bids from several contractors to see how
many bags they specify. Count the number of bags used during installation, either by you
or a contractor, and compare it to the instructions on the bag. The manufacturer should
specify the amount of insulation required to obtain a particular R-value per square foot
(or square meter) of space.
Safety and Health Concerns
Safety Guidelines
Insulation blown into your ceiling cavities should cover the top plate of the wall, but be
sure the eave vents are not covered. These vents provide necessary ventilation to your
attic, and covering them could result in severe moisture problems.
Electrical devices and recessed lights (except "IC-rated" fixtures) require 3
inches (8 centimeters) of clearance from insulation.
Pipes for kitchen stoves, wood stoves, and furnaces should only be insulated with
fiberglass or rock wool because cellulose may smolder if flue temperatures become hot
enough.
Health Considerations
Some observers contend that fiberglass particles can cause cancer if inhaled, and others
state that the fire retardants and insecticides added to cellulose may be harmful to
breathe. While the debate continues as to the health effects of loose-fill insulations, it
is important to protect yourself when installing any type of insulation. Wear a quality
respirator, and wear protective eyewear and clothing such as goggles, gloves, long-sleeved
shirts, and pants to minimize contact with the insulation.
Insulation fibers can also be drawn into air distribution systems if the ducts are not
properly sealed, allowing the fibers to circulate within the living space. Be sure to seal
all of your home's ductwork, as well as any other openings where insulation could leak out
of the wall or ceiling cavities and into your living space.
Conclusion
Cellulose, fiberglass, and rock wool loose-fill insulations are good choices for many
insulation projects. However, they are not suitable for all situations. Conduct careful
research and consider factors such as your climate, building design, and budget when
selecting the best insulation for your specific circumstances. If you control air leakage
and ensure that the insulation you select is installed properly, you can reduce your
energy bills and enjoy a more comfortable home.
Source: U.S. DOE, Energy Efficiency and Renewable Energy Network, Consumer Energy
Information: EREC Reference Brief. EREC is operated by NCI Information Systems, Inc. for
the National Renewable Energy Laboratory/U.S. Department of Energy. The content of this
brief is based on information known to EREC at the time of preparation. No recommendation
or endorsement of any non-U.S. Government product or service is implied if mentioned by
EREC.
|